A little unplanned upgrade this morning. Site is working ok it seems.

Any Electricians Out There?

Post Reply
User avatar
ESquared
Deputy Administrator
Posts: 2911
Joined: Fri Dec 30, 2016 9:00 pm
Location: KC Area
United States of America

Any Electricians Out There?

Post by ESquared » Sun May 19, 2019 11:25 am

First, on scale of 1-10, I'd give myself about a 7 when it comes to DIY household stuff, but I'm never afraid to push the envelope.

That said, electrical panel things kinda give me pause. I'm okay swapping out a light switch, replacing a lamp fixture, etc., but digging into a main panel has been a place I've not gone. Kind of makes YouTube dangerous, with guys diving right in.

Anyway, I have about a 40 year old home, with your basic circuit breakers in the basement, one of which is a 20 amp GFI (I guess) variety, with a white "reset" button. It's connected to outlets that, by today's code should be GFCI outlets, as they're all close to either bathroom sinks or outside on a patio.

I've only been here for a year-and-a-half, but the circuit breaker seems to be failing slowly, as it will trip and won't re-set right away, but, after a few days, seems to be okay, resets and all is good. Makes no sense to me. AND, it seems like the breaker switch is actually damp, another head-scratcher.

SO, the question is, shouldn't I just convert those outlets to GFCI outlets and then replace the circuit breaker with a standard 20 amp breaker?
BB Steel .357 | SGC 22LR | LR .308 | CCH 30-30 | BB Brass .45 Colt (Carbine) | Single Shot 20 gauge | Single Shot .223 | Single Shot 357

User avatar
Mags
Administrator
Posts: 8584
Joined: Fri Apr 13, 2018 9:40 pm
Location: Tualatin Valley Oregon
United States of America

Re: Any Electricians Out There?

Post by Mags » Sun May 19, 2019 11:40 am

.
Yes that is an option. But you don't need a GFCI outlet at every outlet. Just the one closest to the breaker panel in the wired string of outlets. Down stream outlets get wired to the 'load' side of the GFCI outlet.

Its an older home you say so check the wire gauge. Some older homes used 14 gauge wire for outlets and someone later might have replaced an original 15A breaker with a 20A. For 12 gauge wire 20A breaker, 14 gauge wire 15A breaker.
ESquared wrote:
Sun May 19, 2019 11:25 am
...
SO, the question is, shouldn't I just convert those outlets to GFCI outlets and then replace the circuit breaker with a standard 20 amp breaker?
UPDATES: OR passes 114, "one of strictest gun control measures in U.S." https://henryrifleforums.com/viewtopic. ... 34#p213234

tractortad

Re: Any Electricians Out There?

Post by tractortad » Sun May 19, 2019 12:57 pm

It may be cheaper and easier to just replace your panel ckt brkr with another GFCI - that may be why an electrician originally put it there - because he probably put multiple GFCI outlets on that breaker instead of separate branch ckts for outdoor and bathroom. Good call by Mags to check the wiring - I bet your bathroom wiring is not 12ga (rated for 20amp). If it is 14ga(15amp) instead of 12ga you should go with a 15 GFCI ckt brkr. Circuit breakers also should not be damp - which may be the reason that GFCI is tripping - look to see that water is not coming in to your panel through the main feeder lines...

User avatar
cooperhawk
Ranch Foreman
Posts: 5467
Joined: Sat Jan 12, 2019 3:27 pm
Location: 20 miles south of the twin cities.
United States of America

Re: Any Electricians Out There?

Post by cooperhawk » Sun May 19, 2019 1:17 pm

I have also found that GFCI breakers deteriorate over time. I've replaced two that kept breaking and now everything works OK.

PS, not an electrician but when I wire I do get a permit and ask the inspector just what he wants to see, and then I please him.
Retired FAA Air Traffic Control Supervisor
VFW (Life Member), VVA (Life Member)
Legion (Life Member), NRA (Life Member)
U S Army Aviation 64-67, Vietnam MACV 65-66

User avatar
ESquared
Deputy Administrator
Posts: 2911
Joined: Fri Dec 30, 2016 9:00 pm
Location: KC Area
United States of America

Re: Any Electricians Out There?

Post by ESquared » Sun May 19, 2019 1:33 pm

tractortad wrote:
Sun May 19, 2019 12:57 pm
It may be cheaper and easier to just replace your panel ckt brkr with another GFCI - that may be why an electrician originally put it there - because he probably put multiple GFCI outlets on that breaker instead of separate branch ckts for outdoor and bathroom. Good call by Mags to check the wiring - I bet your bathroom wiring is not 12ga (rated for 20amp). If it is 14ga(15amp) instead of 12ga you should go with a 15 GFCI ckt brkr. Circuit breakers also should not be damp - which may be the reason that GFCI is tripping - look to see that water is not coming in to your panel through the main feeder lines...
Thanks for all that. I'll check the wiring when I start to pull the wall outlets out to see what's what.

The weird thing about the "dampness" is that this particular breaker is in the middle of a stack of breakers and I"ve not had any other issues. I'll pull the cover and look for signs of moisture, but can't imagine where it would be coming from...

Gotta pull the cover to replace the breaker anyway!
BB Steel .357 | SGC 22LR | LR .308 | CCH 30-30 | BB Brass .45 Colt (Carbine) | Single Shot 20 gauge | Single Shot .223 | Single Shot 357

User avatar
Mags
Administrator
Posts: 8584
Joined: Fri Apr 13, 2018 9:40 pm
Location: Tualatin Valley Oregon
United States of America

Re: Any Electricians Out There?

Post by Mags » Sun May 19, 2019 2:20 pm

.
If it's just that breaker it could be sweating lubricant off the internal contacts from old age wearout overheating.

Maintenance replacement of a breaker or electrical outlets may or may not require a permit, depending on your local building code.
ESquared wrote:
Sun May 19, 2019 1:33 pm
....The weird thing about the "dampness" is that this particular breaker is in the middle of a stack of breakers and I"ve not had any other issues. I'll pull the cover and look for signs of moisture, but can't imagine where it would be coming from...
UPDATES: OR passes 114, "one of strictest gun control measures in U.S." https://henryrifleforums.com/viewtopic. ... 34#p213234

User avatar
Mags
Administrator
Posts: 8584
Joined: Fri Apr 13, 2018 9:40 pm
Location: Tualatin Valley Oregon
United States of America

Re: Any Electricians Out There?

Post by Mags » Sun May 19, 2019 2:28 pm

.
Maybe, however breakers for some old panels are sometimes hard to find and expensive. Agree that it is best option to replace at the panel.
tractortad wrote:
Sun May 19, 2019 12:57 pm
It may be cheaper and easier to just replace your panel ckt brkr with another GFCI - ...
ESquared wrote:
Sun May 19, 2019 1:33 pm
...
UPDATES: OR passes 114, "one of strictest gun control measures in U.S." https://henryrifleforums.com/viewtopic. ... 34#p213234

User avatar
markiver54
Deputy Marshal
Posts: 11038
Joined: Sun Nov 04, 2018 11:49 am
Location: Biue Ridge Mountains, NC
United States of America

Re: Any Electricians Out There?

Post by markiver54 » Sun May 19, 2019 3:09 pm

GFI & GFCI...same exact thing, as you may know Evan. Both are "Ground Fault Interupters " .
I'm your Huckleberry

User avatar
ESquared
Deputy Administrator
Posts: 2911
Joined: Fri Dec 30, 2016 9:00 pm
Location: KC Area
United States of America

Re: Any Electricians Out There?

Post by ESquared » Sun May 19, 2019 3:19 pm

markiver54 wrote:
Sun May 19, 2019 3:09 pm
GFI & GFCI...same exact thing, as you may know Evan. Both are "Ground Fault Interupters " .
I guess I knew that, but who knows what I know? I dunno!

I'll take a picture of this particular breaker and take it to the store. Very interesting comment about it "sweating."
BB Steel .357 | SGC 22LR | LR .308 | CCH 30-30 | BB Brass .45 Colt (Carbine) | Single Shot 20 gauge | Single Shot .223 | Single Shot 357

User avatar
Mags
Administrator
Posts: 8584
Joined: Fri Apr 13, 2018 9:40 pm
Location: Tualatin Valley Oregon
United States of America

Re: Any Electricians Out There?

Post by Mags » Sun May 19, 2019 8:29 pm

.
ooze, seep; vocabulary alternatives.
ESquared wrote:
Sun May 19, 2019 3:19 pm
markiver54 wrote:
Sun May 19, 2019 3:09 pm
GFI & GFCI...same exact thing, as you may know Evan. Both are "Ground Fault Interupters " .
I guess I knew that, but who knows what I know? I dunno!

I'll take a picture of this particular breaker and take it to the store. Very interesting comment about it "sweating."
UPDATES: OR passes 114, "one of strictest gun control measures in U.S." https://henryrifleforums.com/viewtopic. ... 34#p213234

220
Cowboy
Posts: 1028
Joined: Sun May 13, 2018 11:11 pm
Australia

Re: Any Electricians Out There?

Post by 220 » Mon May 20, 2019 4:58 am

Mags wrote:
Sun May 19, 2019 8:29 pm
.
ooze, seep; vocabulary alternatives.
markiver54 wrote:
Sun May 19, 2019 3:09 pm
GFI & GFCI...same exact thing, as you may know Evan. Both are "Ground Fault Interupters " .
RCD, anyone?

User avatar
ESquared
Deputy Administrator
Posts: 2911
Joined: Fri Dec 30, 2016 9:00 pm
Location: KC Area
United States of America

Re: Any Electricians Out There?

Post by ESquared » Mon May 20, 2019 7:29 am

Mags wrote:
Sun May 19, 2019 8:29 pm
.
ooze, seep; vocabulary alternatives.
ESquared wrote:
Sun May 19, 2019 3:19 pm
markiver54 wrote:
Sun May 19, 2019 3:09 pm
GFI & GFCI...same exact thing, as you may know Evan. Both are "Ground Fault Interupters " .
I guess I knew that, but who knows what I know? I dunno!

I'll take a picture of this particular breaker and take it to the store. Very interesting comment about it "sweating."
Yeah, I get it. Makes sense, since it's the only one in the panel that's a GFI and everything else is bone dry.
BB Steel .357 | SGC 22LR | LR .308 | CCH 30-30 | BB Brass .45 Colt (Carbine) | Single Shot 20 gauge | Single Shot .223 | Single Shot 357

User avatar
BigAl52
Forum Ambassador
Posts: 15048
Joined: Sun Oct 23, 2016 12:43 pm
Location: Evans,Colorado
United States of America

Re: Any Electricians Out There?

Post by BigAl52 » Mon May 20, 2019 8:34 am

Theres alot of sweating that goes on in KC Evan. Just sayin
Don't let the old man in


H001T .22LR
H001T .22LR MONUMENT VALLEY
H003T PUMP .22LR
BBS .41 MAG
SS .357
SIDE GATE 38-55

User avatar
ESquared
Deputy Administrator
Posts: 2911
Joined: Fri Dec 30, 2016 9:00 pm
Location: KC Area
United States of America

Re: Any Electricians Out There?

Post by ESquared » Mon May 20, 2019 10:10 am

BigAl52 wrote:
Mon May 20, 2019 8:34 am
Theres alot of sweating that goes on in KC Evan. Just sayin
NO kidding! I'm the poster-boy for that statement! Not today, though! Cool and calm, but storms on the way.
BB Steel .357 | SGC 22LR | LR .308 | CCH 30-30 | BB Brass .45 Colt (Carbine) | Single Shot 20 gauge | Single Shot .223 | Single Shot 357

User avatar
Mags
Administrator
Posts: 8584
Joined: Fri Apr 13, 2018 9:40 pm
Location: Tualatin Valley Oregon
United States of America

Re: Any Electricians Out There?

Post by Mags » Mon May 20, 2019 10:37 am

.
You have company, likewise. No matter the temp. I lift a finger and start pouring. Have to keep changing out my dew rag for a dry one.
ESquared wrote:
Mon May 20, 2019 10:10 am
BigAl52 wrote:
Mon May 20, 2019 8:34 am
Theres alot of sweating that goes on in KC Evan. Just sayin
NO kidding! I'm the poster-boy for that statement! Not today, though! Cool and calm, but storms on the way.
UPDATES: OR passes 114, "one of strictest gun control measures in U.S." https://henryrifleforums.com/viewtopic. ... 34#p213234

User avatar
ESquared
Deputy Administrator
Posts: 2911
Joined: Fri Dec 30, 2016 9:00 pm
Location: KC Area
United States of America

Re: Any Electricians Out There?

Post by ESquared » Wed May 29, 2019 12:12 pm

DONE!

They're easy enough to pop out of the panel, which means there's no juice running into or out of it, so from there it was "Columbo time."

Original circuit breaker mfr was bought out by Eaton, and, using the Cat. # off of the sticker on the side of the dead breaker (which was still dangling by the wires from the panel), I was able to Google/cross-reference my way to the new Eaton equivalent part number.

Couple of phone calls to local electrical supply shops and scored it this morning.

White and black wires unscrewed from the breaker and the pig-tail ground wire unscrewed from the panel. Reverse the order of screwing down/attaching wires to where they're supposed to go, make sure the switch is in the OFF position, snap it back into the panel, flip it ON and VOILA!

Never even had to turn off the main panel! Who says you can't teach an old dog new tricks!?!
BB Steel .357 | SGC 22LR | LR .308 | CCH 30-30 | BB Brass .45 Colt (Carbine) | Single Shot 20 gauge | Single Shot .223 | Single Shot 357

User avatar
Cofisher
Drover
Posts: 2566
Joined: Sat Mar 26, 2016 8:02 pm
Location: Colorado/Nebraska
United States of America

Re: Any Electricians Out There?

Post by Cofisher » Wed May 29, 2019 12:28 pm

Proud of you boy!
Remember, it's not how many guns you have. It's how many bullets you have.

User avatar
Grunt67
Cowboy
Posts: 1879
Joined: Tue Jan 28, 2020 10:57 am
Location: Hartsville,TN
United States of America

Re: Any Electricians Out There?

Post by Grunt67 » Mon Nov 09, 2020 7:03 pm

I had a GFCI in the kitchen a few months ago, that would trip occasionally. I finally replaced it with a new one, no more problems. I also learned they do deteriorate very time. This had been there since 1991.
FWIW.
I rarely ever buy a rifle, but when I do, it's a Henry.

"Every day above ground, is a good day" ( Al Capone )

User avatar
markiver54
Deputy Marshal
Posts: 11038
Joined: Sun Nov 04, 2018 11:49 am
Location: Biue Ridge Mountains, NC
United States of America

Re: Any Electricians Out There?

Post by markiver54 » Mon Nov 09, 2020 7:20 pm

Yes, found that out myself a couple times. Glad things are back in order!
I'm your Huckleberry

Post Reply